It is my understanding that the industry is moving away from doing live 480V bus ties on Switchgear. Due to NFPA, OSHA and so forth.
It is also my understanding that some sites are not in phase and live buss tieing can be very dangerous in this condition.
My current switchgear contractor just emailed me and told me they are no longer allowed to do it.
So this is all very understandable.
However, my site has 40 substations that were built for live bus tieing. My maintenance guy has been closing bus ties out here for 40 years without incident. They even practice closing live 480V bus ties on a monthly basis to train people. ON several occasions they have even closed EVERY single buss tie on site....with all 40 of our 4160V breakers fully closed. All bus ties perform flawlessly, in perfect phase.
So although this rule is good for most, I don't see how it applies to my site. I feel there is an exception here.
If this rule is actually infused, We will likely have 3 times the amount of shutdowns per year costing big money in production. (no one likes losing money)
What are other people doing in regards to this assuming you have the same in phase switching that I have? Oh ya, our guys ALWAYS wear the full 40 calorie moon suit when switching anything in our switchgear.
I realize this is a touchy subject for the moderators, but I believe it is one that should be openly discussed.
It is my understanding that the industry is moving away from doing live 480V bus ties on Switchgear. Due to NFPA, OSHA and so forth.
It is also my understanding that some sites are not in phase and live buss tieing can be very dangerous in this condition.
My current switchgear contractor just emailed me and told me they are no longer allowed to do it.
So this is all very understandable.
However, my site has 40 substations that were built for live bus tieing. My maintenance guy has been closing bus ties out here for 40 years without incident. They even practice closing live 480V bus ties on a monthly basis to train people. ON several occasions they have even closed EVERY single buss tie on site....with all 40 of our 4160V breakers fully closed. All bus ties perform flawlessly, in perfect phase.
So although this rule is good for most, I don't see how it applies to my site. I feel there is an exception here.
If this rule is actually infused, We will likely have 3 times the amount of shutdowns per year costing big money in production. (no one likes losing money)
What are other people doing in regards to this assuming you have the same in phase switching that I have? Oh ya, our guys ALWAYS wear the full 40 calorie moon suit when switching anything in our switchgear.
I realize this is a touchy subject for the moderators, but I believe it is one that should be openly discussed.