Hey guys/gals, I'm doing a new livestock shed for a customer. We have 2 outdoor waterer/fountains, the manufacturer recommends, buts doesn't require, a ground rod be driven at the waterer. It's a dirt lot, no concrete, so no real equal potential plane. A talk with my inspector suggests not driving the ground rod at the waterer as it could interfere with the rest of my grounding system. So, I already have 2 rods driven at the shed panel. I've run, in 3/4 pvc, #12 to each waterer, I'm wondering if a good idea would be to pull out the #12 green, and instead replace it with a #8 or #6 thhn, and then crimp that to my grounding electrode conductor. 1, because it would be a better connection in the waterer because they're prone to moisture and corrosion. 2, in case they would concrete the yard and I'd need to connect an EPP. Or would this be just overkill at the moment? I do have them connected to GFCI breakers as well. Just wanted another opinon on the matter, thanks!