Toros
Senior Member
- Location
- Tujunga, CA
Hi, I was walking a commercial project, a big print shop, to assess the existing condition or the existing 600A, 3phase, 4w delta, to see if Owner can install a new press machine on line and no need for service upgrading. This is how and what I concluded; The existing loads per peak demand (worst) from local utility company (SCE) is, 150 KW and the new load (press machine) is, 160 KW @240v,3ph. 150 KW + 160 KW=310 KW plus P.F 370 KW or, 896A @ 240V, 3phase Overloading????? But my Alternat. way, 896A / 3 (Above calculated devided 3 legs)=298A draw from each leg not-overloading????? Also , Note this, That I jumped to the roof and measure one of the ungrounded conductor while every 3phase equipments were on and it was 150A . since all loads on that service are 3phase, balanced and I was not sure all loads really were on ,(may be some motors in machines were off) I would says 190A draw avarage each leg . Plus, 128A each leg of new 160 KW machine Plus, safety factor, 28A total: 190+128+28=346A not overloading?????? Thank you