load and emergency feeds in same conduit

Status
Not open for further replies.

pelicanlk

Member
Can the emergency feed & the load wires be in the same conduit of a non-critical or a non life safety panel in a hospital. The chiller in question is 480 volt & has its own transfer switch seperate from essential equipment transfer switch. Therefore it is considered non-essential equipment in considering this.
 
Re: load and emergency feeds in same conduit

Article 700.1, especially the second paragraph explains the requirement for Emergency Systems, FPN # 2 explains some of the equipment that may be on emergency systems.

From NFPA 99:
4.4.2.2.4.1 Separation from Other Circuits. The life safety branch and critical branch of the emergency system shall be kept entirely independent of all other wiring and equipment.

See 700.9(B) and 517.44

Pierre

[ January 19, 2004, 05:09 PM: Message edited by: pierre ]
 