I am trying to figure out the best docking station size to test two parallel gensets. This parallel genset feeds 3 ATS branches:
- optional standby/legally required (combined in one branch)
- emergency (NEC 700)
- critical (NEC 708)
I know that I will not need temp generator connection because the emergency and critical branches can both be supplied by only 1 of the 2 parallel generators.
My question is, if I plan for a docking station that load bank at least 30% of both generators' capacity combined (looking at them as 1 generator), to meet NFPA 110 8.4.2, will I be required to test the separate ATS branches too? Should I plan for load banking each branch separately? If not, I will be testing the generators only, not the ATS's. But I think NFPA 110 requires rotational testing of all ATS's in the EPSS monthly to ensure starting of each, etc. although I think this can be under no load condition.
Thank you!
- optional standby/legally required (combined in one branch)
- emergency (NEC 700)
- critical (NEC 708)
I know that I will not need temp generator connection because the emergency and critical branches can both be supplied by only 1 of the 2 parallel generators.
My question is, if I plan for a docking station that load bank at least 30% of both generators' capacity combined (looking at them as 1 generator), to meet NFPA 110 8.4.2, will I be required to test the separate ATS branches too? Should I plan for load banking each branch separately? If not, I will be testing the generators only, not the ATS's. But I think NFPA 110 requires rotational testing of all ATS's in the EPSS monthly to ensure starting of each, etc. although I think this can be under no load condition.