I honestly don't know a lot of these kind of finer details on medium voltage equipment, but since it is load break equipment I would guess there is an interrupt rating associated with it and it is possibly fine with the higher overcurrent protection as long as it doesn't carry more load than rated for and interrupt rating isn't exceeded? By interrupt rating I mean not just shot circuit/ground fault but also regular switching rating.The NEC applies. The load being fed is a 750kVA xfmr (not fully loaded).
How abut 240.4?First of all, there is no "everything must be protected at it's rating" clause in the NEC.
Which is titled "protection of conductors". Kind of have to assume this means art 310 conductors and not necessarily devices and other connected accessory items.How abut 240.4?
Charlie, note part IX of 240 applies to MV. Again, I am not a MV guy, but it appears the NEC allows OCPD settings for MV to be based on analysis such as conductor damage curves and not just ampacity of the conductor. Note that 240.101 states the setting of a fuse shall not exceed three times the ampacity of the conductor.How abut 240.4?
I am a MV guy. There are actually 3 current ratings. The 200 A is available as load break and non-load break. 600 A is only non-load break. Plus a bunch of voltage classes. It is not dead break. As long as the transformer is unloaded removal is fine, same as a cutout. Plus unless you absolutely need load break I recommend against them. If you read the specs carefully they can require up to 150 lbs of force to remove where non-load break is half that. When the load break elbows get a little “seasoned” they take a two man crew or one man and a tow strap to remove.
A fuse rating may mean something when it protects a power cable but it is quite another thing when it is protecting an inductive load. They are never rated for 100% of the continuous duty rating due to inrush and temporary overloads. They will trip every time on startup. Effectively the downstream protection protects from overloads and the upstream protects against short circuit. So you really need to look at the continuous duty rating of the system not just the high side.
S&C (sandcastle.com) has a free program called Coordinaide that plots fuse curves for MV power fuses and transformer damage and magnetization curves for MV. It saves a lot of headaches if you don’t have access to power system analysis software and need to size fuses to avoid nuisance tripping.
I am a MV guy. There are actually 3 current ratings. The 200 A is available as load break and non-load break. 600 A is only non-load break. Plus a bunch of voltage classes. It is not dead break. As long as the transformer is unloaded removal is fine, same as a cutout. Plus unless you absolutely need load break I recommend against them. If you read the specs carefully they can require up to 150 lbs of force to remove where non-load break is half that. When the load break elbows get a little “seasoned” they take a two man crew or one man and a tow strap to remove.
A fuse rating may mean something when it protects a power cable but it is quite another thing when it is protecting an inductive load. They are never rated for 100% of the continuous duty rating due to inrush and temporary overloads. They will trip every time on startup. Effectively the downstream protection protects from overloads and the upstream protects against short circuit. So you really need to look at the continuous duty rating of the system not just the high side.
S&C (sandcastle.com) has a free program called Coordinaide that plots fuse curves for MV power fuses and transformer damage and magnetization curves for MV. It saves a lot of headaches if you don’t have access to power system analysis software and need to size fuses to avoid nuisance tripping.
Where does one find 600 amp connectors? Is it just a matter of doing the math? Looks like for 15 kv class you would need a monster 5000 kva to need one. At 4160 of course you get there much sooner, 1,400KVA.30+ years of pulling elbows we have never had an elbow that required a “towstrap”. They never get that sealed. That’s why they make slide hammers.
And with the newer design you don’t have to worry (as much) about partial vacuum flashover on the load break elbows.
The manufacturer calls 600 & 900 dead break. We will not take them off hot. I would really hate to drop that bolt out with a dead break elbow and have to put it back on with 14,000 volts (or even 4160) while standing on the ground. Only a fool would try that.
As far as fusing, a 100T will hold 400 amps for 5 seconds, 1000 amps for 42 cycles. Plenty of time for inrush to settle down.
I think a bigger problem may be getting the fuse selection on a transformer that size to coordinate with the utility protection.
They can be ordered easily enough.
200 amp loadbreak elbows, around $30-50 apiece. I think we pay about 25-28 because we use so many.
600 amp kits.. $75
Think feeders with several transformers rather than just one.
or entire circuits with about 100 transformers in the75-1500 kVa range.
The cable size is #3/0.IMO the cable terminations and joints should match the cable ampacity.
What size cable are you using?
I know that 600 Amp non-load break elbows do have a short time overload rating on some manufacturer's equipment. For some Eaton products the overload allowed on a 600 amp elbow is 1000 amps for 24 hours.I'm reviewing a submittal for load break elbows on a 4160V system. The contractor is proposing 200A elbows, but the upstream protection is 250A fuses. Any concerns with using these elbows?