I've been asked to verify that a 40 KW generator will power a trailer set up as a commercial kitchen. Their load is
21 each 120v, 14 amp microwaves
3 each 120v, 7a freezers
1 each 120v, 14a Air Conditioner
existing lighting load of 120v, 10a
Total load is 40,680 VA
It looks to me that a 40KW generator will work fine especially after the demand factors are applied. Can anyone give me code references for applying demand factors and such?
An engineer said that the load has to be calculated by multiplying by 240v but I disagree since all the loads use 120v. If there were 240v loads then those would individually be calcualted and applied to the total.