Load calc for a DC motor with armature and field current

Status
Not open for further replies.

jaraujo1

Member
I need to calculate KVA for a 100HP DC motor, with the following characteristics:
Armature:148 amps@500VDC
Field:2.38amps@300VDC
Base speed: 1750 RPM
I have not been able to find information on how the armature and field current/votage interact to figure out the KVA. Any information will be appreciated.

Juan
 

coulter

Senior Member
Normally one does not see the terms "kva" and "DC" in the same thought.

The short answer is pretty simplistic:
Armature is 148A X 500V = 74,000va = 74kva = 74kw
Field is 2.38A X 300V = 714va = .741kva = .741kw

And you likely already knew this.

So, I'm guessing you are more interested in the power required for the two power supplies you will have to have - one for the field and one for the armature.

For that, I would suggest checking the power supplies nameplate data for input power - or call the mfg. Thjere are no rules of thumb I know of.

carl
 

rootboy

Member
Location
Tennessee
Unless you are going to design your own DC drive, or unless you are installing this motor somewhere that still has 500VDC available, I would just select a 100hp drive from your favorite local supplier.

Or am I missing something? (not being sarcastic, just wondering).
 