RichB
- Tacoma, Wa
- Electrician/Electrical Inspector
Good morning all,
Here is another test question and the 3 ways it is worked
Number 1 is directly from the test and numbers 2 and 3 are the two ways I worked it--cuz I am having a senior moment and just can't remember or find it in code.
Number one does not take into account the # of CCA, and here is my senior moment--I can't remember if we do or not with parallel runs. As the question stands I would read it to mean in conduit and to do a complete calculation.--As always TIA folks!
1. For a service with 9 parallel runs of XHHW 750 kcmil copper per phase, all run in an ambient temperature of 100? - 102? F., what is the total ampacity to each phase? Answer: __________________________
Answer: 3762 amps [Ref: 750 kcmil wire is rated at 475 amps. (9)(475)(0.88) = 3762 amps]
2.
Example #1
9 sets of 750 KCML CU
Below using 75 degree column in both conductor and adjustment
750 KCML CU = 475 amps @ 75 degree column, x .70 conductor fill = 332.5 amps x .88 correction factor 75 degree column = 292.2 x 9 sets = 2633.4 amps
3.
Example #2
Below using 90 degree column in both conductor and adjustment
750 KCML CU = 535 amps @ 90 degree column, x .70 conductor fill = 374.5 amps x .91 correction factor 90 degree column = 340.7 x 9 sets = 3067.1
2.
Example #1
3.
Example #2