16 Welders
16 Welders
IMO all the welders would have the same load current based on Table 630.11(A)
Depending on the type of welder that would be 73amps x .84 or .86 to get the load for one welder. 630.11(B) says the minimum load would be based on the 70% duty cycle load of each welder. So using the 73amps x .84= 61.32 amps per welder.
According to 630.11(B) the first two at 100%= 122.64amps, the third at 85%=52.12amps, the fourth at 70%=42.92amps and the balance of 12 at 60%=441.50amps for a total of 659.18 amps. See the Exception and FPN. The actual load will have alot to do with how all these welders are really going to be used. I used the 73amps you listed if its 50amps then the load will be lower but I think the process is correct. Hope this helps..