We have a small job in the office (on a large existing building) that calls for a very simple face lift in a circulation area of a university building. We are essentially demo'ing 3 existing 100W incandescent luminaires and a few outlets, and then adding 3 LED can lights and a few new outlets. My coworker is stressed about having to prove the load on the distribution system all the way back to the point of service, as we do not have good information on the calculated or demand load in order to perform a comprehensive load calculation, nor do we have the time for the 30 day metering. So here's my question:
I seem to recall an exemption in the code that states that if the new load on the branch panelboard does not exceed more than 5% of the panel's bus rating, that load calculations for feeders and equipment up-stream of that panel are not required. Is this correct, or some bad information I received early on from my early mentors? I can't seem to find this anywhere in the code (NEC2014). Any insight would be appreciated.
Thanks,
kW
I seem to recall an exemption in the code that states that if the new load on the branch panelboard does not exceed more than 5% of the panel's bus rating, that load calculations for feeders and equipment up-stream of that panel are not required. Is this correct, or some bad information I received early on from my early mentors? I can't seem to find this anywhere in the code (NEC2014). Any insight would be appreciated.