Dear Engineers,
Thank you for the awesome forum.
I got some answers from the already posted threads. but I have this one to clearify.
Lets say,
I have a 10 Ton Package unit to install [3phase 380V] and supply power.
should my calculation look like this:
KW= 10*3.51
A=35.1/(1.732*380) [lets say p.f is 1]
A=53.3A
Now, is it okey to select Circuit breaker and Cable according to this value of 53.3 A,
say 63A with 4C 25 sq-mm.
Or I am missing things??
I went through the forum and looks like I am missing alot.
Thank you