I need help to calculate the load (in Amps) to the electrical panel of each of two existing building (see attached the description for the upgrade required and data sheet related to this equipment to be added).
ELECTRICAL Data for Heat Pumps/BOSCH
Added Load to Building-1
1 x Model 067 Heat Pump
1 x Mode 049 Heat Pump
1 x Mode 025 Heat Pump
13 Fan coil units – each with 0.2 HP fan motor
2 x 1 HP Hot/Chilled Water pump motor
2 x 5 HP Condenser water pumps
Added Load to Building-2
2 x Model 067 Heat Pump
10 Fan coil units with 0.2 HP fan motor each
2 x 0.5HP Hot/Chilled Water pump motor
TW R-454B Model Series Residential Water to Water Heat Pumps:
Model 067: Voltage/HZ/Phase= 208-230/60/1; Voltage Min/Max = 197/253; Compressor/RLA=25.2; Compressor/LRA= 147.3; Min. Circuit Amps= 31.5; MOP CAL= 56.7; MOP= 50
Model 049: Voltage/HZ/Phase= 208-230/60/1; Voltage Min/Max = 197/253; Compressor/RLA=18.3; Compressor/LRA= 138; Min. Circuit Amps= 22.9; MOP CAL= 41.3; MOP= 40
Model 025: Voltage/HZ/Phase= 208-230/60/1; Voltage Min/Max = 197/253; Compressor/RLA=10.3; Compressor/LRA= 62.0; Min. Circuit Amps= 12.8; MOP CAL= 23.1; MOP= 20