I wanted to post these questions again since I've not seen a response from Saturday's forum yet.
This condo shares a common 3/0 feeder with three other units protected by one 200 amp breaker located in a panel board below. The feeder runs through 2'' EMT into and through a 200 amp sub-panel located in each unit. The 3/0 feeder is tapped with a # 4 THHN that terminates on the main lugs of each sub-panel. We are bidding a remodel of one unit - they are adding a stackable washer dryer and two HVL's and additional lighting. The Heat and A/C are not factored in the calculation as the building has a water chilled system. Each original unit's load calc. is aprox. 52 amps (Optional calc)
and the aprox. calc for the remodel unit is 64.
Does table 220.84 apply to determine the feeder size for these units- If so the feeder would not need to be changed. What other code articles should be considered? 240.86 seems to indicate an Engineer's seal will be needed before any design can be determined but I am not sure if this applies in this situation. Also, the panel is shown on the drawings to be relocated further than 25' from original location. Any good advise will be greatly appreciated. -Rich
This condo shares a common 3/0 feeder with three other units protected by one 200 amp breaker located in a panel board below. The feeder runs through 2'' EMT into and through a 200 amp sub-panel located in each unit. The 3/0 feeder is tapped with a # 4 THHN that terminates on the main lugs of each sub-panel. We are bidding a remodel of one unit - they are adding a stackable washer dryer and two HVL's and additional lighting. The Heat and A/C are not factored in the calculation as the building has a water chilled system. Each original unit's load calc. is aprox. 52 amps (Optional calc)
and the aprox. calc for the remodel unit is 64.
Does table 220.84 apply to determine the feeder size for these units- If so the feeder would not need to be changed. What other code articles should be considered? 240.86 seems to indicate an Engineer's seal will be needed before any design can be determined but I am not sure if this applies in this situation. Also, the panel is shown on the drawings to be relocated further than 25' from original location. Any good advise will be greatly appreciated. -Rich
Last edited: