I was looking at the spec sheet for a heat pump, they have a 12kW input rating under the rated cooling section and 13kW under rated heating ( this was a 208V,3Ph unit ), is this the actual load if not what do they represent? I.e. do I just take the bigger of the two (i.e. 13kW),
I remember that the there was a current rating(cant remember if it was fla or mca or rla) as well, for loading do I go 208x1.732xcurrent rating ?
As a rule of thumb to get a general idea of the load on a mechanical unit which current value does one take to multiply with voltage and 1.732?
I remember that the there was a current rating(cant remember if it was fla or mca or rla) as well, for loading do I go 208x1.732xcurrent rating ?
As a rule of thumb to get a general idea of the load on a mechanical unit which current value does one take to multiply with voltage and 1.732?