Load calculation for Heat Pump

Status
Not open for further replies.
I was looking at the spec sheet for a heat pump, they have a 12kW input rating under the rated cooling section and 13kW under rated heating ( this was a 208V,3Ph unit ), is this the actual load if not what do they represent? I.e. do I just take the bigger of the two (i.e. 13kW),

I remember that the there was a current rating(cant remember if it was fla or mca or rla) as well, for loading do I go 208x1.732xcurrent rating ?

As a rule of thumb to get a general idea of the load on a mechanical unit which current value does one take to multiply with voltage and 1.732?
 
To be accurate, I'm afraid you might need to refer to the manufacturers cut sheet or nameplate data.
Some 3 phase units have single phase motors which will cause some current discrepancies, also, different units may allow a portion of the heat to operate in conjunction with the compressor so it's not always and either/or load..

208X 1.732 would give you the equivalent 3 phase voltage so you can get some idea.
 
In short you need 2 things off the nameplate. MCA determines conductor size and MOCP determines breaker or fuse size. The manufacture should provide all that.

Gus was quicker.

And voltage, freq, and phase. I added this before someone nails me.
 