I was doing a practice test, and the question was figure out the load for a bunch of stuff.
A 208-volt, three-phase feeder is to supply the following loads:
Two, 5-HP three-phase induction motors,
one, 3-HP single-phase 208 induction motor,
general lighting for a 150' x 100' office area,
92, 120-volt receptacles in the office area.
I understand how to calculate everything except for the receptacles. The solution has me take the receptacle load, the larger of 220.14.K (1) or (2), which is 16,560 VA, and divide it by the voltage to find the amperage.
Their math shows 16,560 / (208 * √3)
My question is, why am I using 208 for the voltage for the receptacles when the question states they are 120 volt?
Thanks for the tips!
PS: Their answer is 276 Amps.