I got a call from a general contractor who was using a different EC. Their blue prints and other forms were declined. This is to be a fitness club with 8 low bays 400 watts / 4.5 kw waterheater / 40 receptacles / 2 ac units with 15 Kw heat each / 2 vents for bathrooms and 2 recessed lights above showers.my question is to look at what he submitted and tell me where he got his numbers from and what he did right and what he did wrong.
3750 Sq ft geleral lighting load 11.25kw
9 120v equipment outlets 13.5 kw
2 120v bathvents 3.0 kw
1 120v sign circuit 1.5 kw
1 240v water heater 4.5 kw
=
33.75 kw
- 10.00 kw
=
23.75 kw
x .4
=
9.50 kw
+10.00 kw
=
19.50 kw
+ HVAC 30.00 kw
=
49.50 kw
120 / 208 / 3ph 24.75 = 118.00 amps
Thanks Dr Will confused master in texas
P.s I will show my work later.