Can someone help me to calculate the load for this branch circuit.
I have 15 servers in one rack.
13 of them are pulling 8 amps at 208V if fully loaded.
The other two are pulling 24 amps at 208V if fully loaded.
The calculation I have are as follows:
8 x 208 = 1664VA x 13 = 21632VA
12 x 208 = 2496VA x 2 = 4992VA
Total VA = 26624VA
Article 645-5(a) Tells me I SHALL have an ampacity of not less then 125% of the total connected load.
26624VA x 1.25 = 33280VA
Is there a section of Article 210 that allows me to derate this load, because all servers will never be 100 % loaded?
Thanks for your help
Kevin