What is a ‘reasonable” load to assign to a residential outbuilding that the owner wants a 100A sub feed installed in.
Using a full load in the calculation always jacks it up to a seemingly ridiculous number.
Most always bumping into a 320/400A meter base.
Our utility has 100 and 200A meter bases available on a walk basis.
Larger ones now need “design criteria” and take weeks to get.
Is using the first 10K watts at 100%
and the balance at 40% reasonable?
Opinions welcome