load calculation

Status
Not open for further replies.

MBLES

Senior Member
i used mike holt excel spreadsheet residential load calculation. I just wanted to get a 2md 3rd 4th opinion on it..

I have 3185 sqft home 3br3bath with all minimum requirements on electrical except a few.

refrigerator
microwave
20a gfci each bath 3 total
range hood 1200va
2-2ton ac 2850 ea.

other than an elevator that will be onsite and i wont know off hand. What else am i over looking for residential load calculation??

Mike Holt Calculation reads Service demand 13190va w/ 63a and 63a neutral 100a minimum service. I know this will change once elevator is calculated but without calculation does this look Right?? Thanks
 

MBLES

Senior Member
That seems a little low -- take a look at 220.82


I put those numbers in mike holts residential calculator. Those are numbers that came out. I put in sqft house then 2 spbc and laundry plus the ones i listed. Thats the load that came up. What do you think im missing??
 

Smart $

Esteemed Member
Location
Ohio
The microwave, refrigerator, and bathroom receptacles can all be included with general lighting under 220.52 and 220.14(J)(1).
 

MBLES

Senior Member
The microwave, refrigerator, and bathroom receptacles can all be included with general lighting under 220.52 and 220.14(J)(1).


Yes I understand. When i put all those numbers in the calculator or even paper. I get around 60a for a 3178sqft home. Does that sound about right to you?? Is there something you think im missing?? the house is a basic home norhing special.
 

Smart $

Esteemed Member
Location
Ohio
Yes I understand. When i put all those numbers in the calculator or even paper. I get around 60a for a 3178sqft home. Does that sound about right to you?? Is there something you think im missing?? the house is a basic home norhing special.
I don't do residential, so nothing and everything sounds about right to me... :D
 