Load Calculation

Status
Not open for further replies.

Electriman

Senior Member
Location
TX
Greetings,

I have a project that has a couple motors and some other continues and non-continues loads. Some of the motors have VFDs. I have following options for load calculations:
A) I can use NEC 215 which says 125% of continues load plus 100% of non continues loads. The load can be motor too.
B) I can use NEC 430 to calculate the motor load and add 125% of continues and 100% of non-continues loads other than motors

What do you recommend?

As far as motors with VFD, should I consider the motor hp for load calculation or VFD input current?


Thanks in advance.
 
I see no reason to base the load calculation on the VFD input rating. Often the VFD has a horsepower rating that exceeds the horsepower of the motor that is being used. The VFD will never pull its rated input current in that type of applicator. The actual load is the motor and the small amount of losses in the VFD. I would use the motor currents as shown in the Article 430 tables for the load calcualtions.
 