Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Hello.
I have the (5) worker trailers that I need to feed with temp. (4) have 60MCB and (1) has 100A MCB.
I walked the site today to try and determine where I could pull power from.
There is only 277/480 available from a panel( see pic). Our plan is to run a feeder from this panel( use a transformer to get 120/208v) to a temp panel by the trailers and then feed the trailers from the temp panel.
A few questions.
1. How do I determine what size temp panel i would need for the trailer. Is it just adding up 60Ax4 and 100A. ...340A?
2. I guess once I determine the temp panel size then I can determine if the existing panel(277/480v) has enough power available to feed the temp panel.
A 75kva xfrm would give me 208amps on the step down side and a 112.5 would give me 312amps on the step down side. Again I need to know what size temp panel(main breaker) I'd need to feed those trailer.
Also with either of those size xfrmrs I'd need either a 125A or 175A OCPD in the existing panel( in the pics). Not sure If I have that power available. Can one tell just by looking at the breakers and panel schedule?
I have the (5) worker trailers that I need to feed with temp. (4) have 60MCB and (1) has 100A MCB.
I walked the site today to try and determine where I could pull power from.
There is only 277/480 available from a panel( see pic). Our plan is to run a feeder from this panel( use a transformer to get 120/208v) to a temp panel by the trailers and then feed the trailers from the temp panel.
A few questions.
1. How do I determine what size temp panel i would need for the trailer. Is it just adding up 60Ax4 and 100A. ...340A?
2. I guess once I determine the temp panel size then I can determine if the existing panel(277/480v) has enough power available to feed the temp panel.
A 75kva xfrm would give me 208amps on the step down side and a 112.5 would give me 312amps on the step down side. Again I need to know what size temp panel(main breaker) I'd need to feed those trailer.
Also with either of those size xfrmrs I'd need either a 125A or 175A OCPD in the existing panel( in the pics). Not sure If I have that power available. Can one tell just by looking at the breakers and panel schedule?
Attachments
Last edited: