How would you calculate the load for 32 ranges at 18kW ea. Using table 220.55.
The title of the column is kind of misleading..."(Not over 12 kW Rating)"1. Over 12 kW through 27 kW ranges all of same rating. For ranges individually rated more than 12 kW but not more than 27 kW, the maximum demand in Column C shall be increased 5 percent for each additional kilowatt of rating or major fraction thereof by which the rating of individual ranges exceeds 12 kW.
celtic said:By using Note on :
Column C Maximum Demand (kW) (See Notes) (Not over 12 kW Rating)
The title of the column is kind of misleading..."(Not over 12 kW Rating)"
LOL.Dennis Alwon said:Thanks celtic I knew that but obviously had a senior moment.
Affirmative.Isidro Molina said:18kv - 12kv=6kv
6kv X 5% =30%
15kv + 32kv=47kv
47kv X 30%=61.1kv
am I doing this right?