Did I do this right? I have 3- small apartments and 1- ice cream store in a building. I am attempting to do a load calculation to figure my mininum service size. I calculated the following:
ICE CREAM STORE 1482 SQ FT X 3 VA = 4446
ICE MACHINE 1080
COOKIE MACHINE 1350
SOUP WARMER 1200
REFRIGERATOR 1100
ICE CREAM MACHINE 5000
ICE CREAM MACHINE 5700
FREEZER 600
COFFEE 1800
REFRIGERATOR 600
EXPRESSO 4000
WASHER 1200
DRYER 5000
WATER HEATER 4500
TOTAL 37576
10000
REMAINDER @ .40 PERCENT 11030
20 KW HEAT @ .40 = 8000
TOTAL 29030
29030 / 240 = 121 AMPS
APARTMENTS POTENTIAL OF 3 APARTMENTS (2-EXISTING, 1- FUTURE)
525 SQ FT EA X 3VA= 1575
RANGE 8000
STACKED WASHER/DRYER 5000
WATER HEATER 4500
DISH WASHER 1200
TOTAL 20275
10000
REMAINDER @ .40 PERCENT 4110
2000 VA HEAT @ .40 PERCENT 800
TOTAL 14910
14910 / 240V = 62 AMPS
3 APARTMENTS (2-EXISTING, 1- POSSIBLY FUTURE) 62A X 3 = 186 AMPS
STORE/ICE CREAM 121 AMPS
TOTAL LOAD 307 AMPS
Is this correct? Thank you, dhobdey1
ICE CREAM STORE 1482 SQ FT X 3 VA = 4446
ICE MACHINE 1080
COOKIE MACHINE 1350
SOUP WARMER 1200
REFRIGERATOR 1100
ICE CREAM MACHINE 5000
ICE CREAM MACHINE 5700
FREEZER 600
COFFEE 1800
REFRIGERATOR 600
EXPRESSO 4000
WASHER 1200
DRYER 5000
WATER HEATER 4500
TOTAL 37576
10000
REMAINDER @ .40 PERCENT 11030
20 KW HEAT @ .40 = 8000
TOTAL 29030
29030 / 240 = 121 AMPS
APARTMENTS POTENTIAL OF 3 APARTMENTS (2-EXISTING, 1- FUTURE)
525 SQ FT EA X 3VA= 1575
RANGE 8000
STACKED WASHER/DRYER 5000
WATER HEATER 4500
DISH WASHER 1200
TOTAL 20275
10000
REMAINDER @ .40 PERCENT 4110
2000 VA HEAT @ .40 PERCENT 800
TOTAL 14910
14910 / 240V = 62 AMPS
3 APARTMENTS (2-EXISTING, 1- POSSIBLY FUTURE) 62A X 3 = 186 AMPS
STORE/ICE CREAM 121 AMPS
TOTAL LOAD 307 AMPS
Is this correct? Thank you, dhobdey1