industrial1003
Member
- Location
- Easton Pennsylvania
I am looking to add an industrial machinery load (multiple machines) to an existing facility, and am finding the code (NEC 670) good at spelling out the supply conductor and Feeder OCPD portions for industrial machinery installation. My issue is that I need to calculate the proposed new building load for a permit submission package. I have nameplate data but am wondering if that FLC needs to be multiplied by 125% since the machine will be considered a continuous duty load on the buildings electric system. NFPA 79 only requires the FLC of all devices operating at the same time for nameplate data so not sure how they set their values assuming minimum requirements. Any advice would be appreciated as I have spent a few hours now going back and forth between 670 and 220 without really making a solid determination.
Example machine data would be:
1 machine 480V 40A FLC nameplate 3 phase
2 machines 480V 15A FLC nameplate 3 phase
1 machine 480V 25A FLC nameplate 3 phase
KVA at 100 % listed comes out to:
1 X 33255 VA
2 X 12471 VA
1 X 20785 VA
Total KVA = 78982 VA = 78.982 KVA
KVA at 125% listed comes out to:
78.982KVA X 1.25 = 98.7275 KVA
Example machine data would be:
1 machine 480V 40A FLC nameplate 3 phase
2 machines 480V 15A FLC nameplate 3 phase
1 machine 480V 25A FLC nameplate 3 phase
KVA at 100 % listed comes out to:
1 X 33255 VA
2 X 12471 VA
1 X 20785 VA
Total KVA = 78982 VA = 78.982 KVA
KVA at 125% listed comes out to:
78.982KVA X 1.25 = 98.7275 KVA