How would you do a load calculation for a barn? I don't see it specified in the code anywhere. Barn is primarily storage but will need general lighting and receptacles.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
How would you do a load calculation for a barn? I don't see it specified in the code anywhere. Barn is primarily storage but will need general lighting and receptacles.


Only way I know of is to know the loads that will be used. There is no load calculation, standard or optional, in the NEC for a barn that I'm aware of.
 

crispysonofa

Senior Member
Location
New England
Occupation
Electrical and Security Contractor
Thank you for the reply, I didn't see one either which is what sparked my interest. Would I calculate all the loads with a power factor of 100%?
 

Smart $

Esteemed Member
Location
Ohio
JMO but you can consider a barn as "Warehouses (storage)" if it is in fact used for nothing more than storage...

...or you can calculate by using connected load. Lighting per 220.14(D) or (E). Receptacles per 220.14(H) or (I).
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
We do them based on owners input and our own experience with some added fudge factor=highly scientific load calc.:cool:
 

just the cowboy

Inactive, Email Never Verified
Location
newburgh,ny
Watchout.

Watchout.

I see you are from New England, DON'T rely on the home owner alone. They don't know what a bucket heater 100w - 1000w for a stall draws, they just say it won't be much. Most put in water heaters in each stall and a tank heater 1250w-1500w outside plugged in to the barn.