Load Calculations for Existing Panelboard

Status
Not open for further replies.

shull

Member
Location
Boulder Colorado
Can someone advise me on Article 220.60. I have 4 Dock doors & 4 Dock Ramp levelers on separate circuits. 2 are used for 5 minute intervals about 3 times each day. The one at shipping & one at receiving. Can I use 220.60 in calculating the load for an existing Panelboard. To get a permit for a 20 amp circuit the authority wants a load calculation for the Panelboard. Can I use 1 of the opener & ramp or do I have to use all 8 circuits in my calculation? Thanks Ron



Sent from my 0PJA2 using Tapatalk
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
In my opinion, if all 8 branches supply motors then art.220.50 it is more suitable.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
First step: Count all 8, including the largest at 125%. Then add the rest of the loads on the panel. Is there enough remaining spare capacity to handle one more 20 amp circuit? If so, submit it that way, and call it good.

Second step: If the above process yields a calculated load higher than the rating of the panel, then you need to make some assumptions. If a motor runs for only 15 minutes a day, then I believe you can make a case for non-coincident loading with other motors.
 