jglavin427
Member
- Location
- Denver, CO
When performing a load calculation for a panel, I always limit the total demand load to less than the transformer rating. I'm reviewing a set of drawings where they are proving the panel based on the demand being less than the main breaker (but more than the transformer rating).
The job has a number of transformer/panel calculations, but just an example of one where I saw this: Load summary shows existing load at 138.5kVA, New load of 16.7kVA, for a total of 155.2kVA on a 150kVA transformer. They are asserting that with this 431A of load, the 500A MCB panel still has 69A of spare capacity.
What are your thoughts?
The job has a number of transformer/panel calculations, but just an example of one where I saw this: Load summary shows existing load at 138.5kVA, New load of 16.7kVA, for a total of 155.2kVA on a 150kVA transformer. They are asserting that with this 431A of load, the 500A MCB panel still has 69A of spare capacity.
What are your thoughts?