Load Calculations for Show Windows

Status
Not open for further replies.

wdingman

Member
Location
Chicago
Occupation
Electrician
I am reviewing various exam preparation materials for my apprentices. I have discovered a difference of opinion when it comes to determining the calculated load for show windows:
  • Mike Holt's Illustrated Guide to Electrical Exam Preparation (2017 edition) does not add an additional 25% to the show window calculation based on the 200 VA per linear foot of show window (see page 496). The book does not say anything about the load being continuous or non-continuous. The illustration, however, is of a store so it would seem safe to assume that the load is continous.
  • In Ray Holder's Calculations: 2020 National Electrical Code, the author adds an additional 25% to the show window calculation. (See Exam 2, question 9). He adds this because the load is continuous.
Which of these approaches is correct?
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
I am reviewing various exam preparation materials for my apprentices. I have discovered a difference of opinion when it comes to determining the calculated load for show windows:
  • Mike Holt's Illustrated Guide to Electrical Exam Preparation (2017 edition) does not add an additional 25% to the show window calculation based on the 200 VA per linear foot of show window (see page 496). The book does not say anything about the load being continuous or non-continuous. The illustration, however, is of a store so it would seem safe to assume that the load is continous.
  • In Ray Holder's Calculations: 2020 National Electrical Code, the author adds an additional 25% to the show window calculation. (See Exam 2, question 9). He adds this because the load is continuous.
Which of these approaches is correct?
IMHO, The load should be calculated as continuous. Since most commercial lighting is continuous. I personally have not seen many residential units with a sizeable show window. :)
 

webmaster

Administrator
Staff member
Location
Leesburg
Occupation
System Admin
I am reviewing various exam preparation materials for my apprentices. I have discovered a difference of opinion when it comes to determining the calculated load for show windows:
  • Mike Holt's Illustrated Guide to Electrical Exam Preparation (2017 edition) does not add an additional 25% to the show window calculation based on the 200 VA per linear foot of show window (see page 496). The book does not say anything about the load being continuous or non-continuous. The illustration, however, is of a store so it would seem safe to assume that the load is continous.
  • In Ray Holder's Calculations: 2020 National Electrical Code, the author adds an additional 25% to the show window calculation. (See Exam 2, question 9). He adds this because the load is continuous.
Which of these approaches is correct?
That example follows the style of Annex Example D3 and is for the "Demand Load" value required by 220.14(G)(2) not the branch circuit or service load @125%. The Example in 11.9 shows the additional 125% added for a continuous load. If you have any other questions or suggestions feel free to email me Brian@MikeHolt.com - Brian House
 