I am reviewing various exam preparation materials for my apprentices. I have discovered a difference of opinion when it comes to determining the calculated load for show windows:
- Mike Holt's Illustrated Guide to Electrical Exam Preparation (2017 edition) does not add an additional 25% to the show window calculation based on the 200 VA per linear foot of show window (see page 496). The book does not say anything about the load being continuous or non-continuous. The illustration, however, is of a store so it would seem safe to assume that the load is continous.
- In Ray Holder's Calculations: 2020 National Electrical Code, the author adds an additional 25% to the show window calculation. (See Exam 2, question 9). He adds this because the load is continuous.