Jammer310

Member
Mike,
Inspectors in our county area requires us to include 100% demand load on both compresors and air handler for Service load calculations as referanced in (2002 NEC 220.30) I know still.

Now on the 2005 NEC this article shows its been revised.
Article 220.82(C)4

Question: Can I calcutate 100% demand load for the compresor and 65% on the Air Handler?

thanks
jammer310
 
Jammer310 said:
Mike,
Inspectors in our county area requires us to include 100% demand load on both compresors and air handler for Service load calculations as referanced in (2002 NEC 220.30) I know still.

Now on the 2005 NEC this article shows its been revised.
Article 220.82(C)4

Question: Can I calcutate 100% demand load for the compresor and 65% on the Air Handler?

thanks
jammer310
From the 2005 NEC:

220.82(C) requires the largest of the six selections.

220.82(C)(2) identifies 100 percent of the nameplate rating of the heating when a heat pump is used without any supplemental heating. That would include the air handler.

The air handler has to be working for the compressor to be working, except maybe for a brief period at startup. I don't see any realistic justification for eliminating the air handler load. That would be like trying to eliminate the load of the fan in the evaporator/condenser unit because it isn't the compressor.
 
The fan and controls in the air handler are almost trivial (1KW or so) compared to strip heat, and variable speed air handlers rarely draw nameplate amps. But I agree it needs to be included at 100% ONLY IF there is not supplemental strip heat (which is typically 7KW to 20 KW). The strip heat is a killer, and I see no reason why it shouldn't be treated any differently than a pure electric furnace. Doing 20 KW of strip heat at 100% makes no sense to me, as it rarely runs at full tilt, especially if the compressor is still running.

So if you have a heat pump with strip heat, it seems reasonable to me to use the compressor MCA plus the air handler MCA. Note that modern HVAC components use a 125% nameplate value and typically use the term MCA on both the airhandler and the compressor. I'm glad this was fixed in 2005, as it creates quite a bit more capacity on my service (30 amps).
 