ESolar
- Eureka, CA Humboldt County
- Electrician/Contractor
Two questions regarding panel sizing with solar and breaker placement. 200A service and panel. Solar feed required derating to 175A.
1. When doing load calcaultions for additional appliances, EV charger etc., is one limited to 175A, or can one still use the 200A limit of the panel and feeder. And if you're limited to 175A, is that answer due to safety concerns? I thought, maybe naively, that the solar output (if any) would offset the demand, which is why the solar OCPD is usually placed at the far end of the bus bar and the bus bar is protected by the main OCPD.
2. Suppose the solar is on a subpanel along with an EV charger. At night it is an EV load, and during the day it is a solar feed. Where is the optimal/proper location for the subpanel feeder/OCPD in the main? (note that, although not important for this question, in the subpanel the solar OCPD is at the far end)