Hello all,
I am working on some service load summary calculations for a mixed use building and had a few questions.
I currently have 3-phase 4 wire incoming service that will feeder a 3phase meter bank and single phase downstream residential panels.
Now when sizing a service using the service load calculations are you just sizing the incoming service conductors or do you also size the service tap conductors. Lets say my service calculations for a meter bank and house panel are 260A and the commercial space is 95A. Now I want to remove the house panel from the meter bank and do a direct taps on a wire trough to the service conductors. Is the meter bank tapped at 300A or can I downsize to 250A because I removed the house load and will do a separate service tap. Note I am running the service conductors into a wire trough and service tapping for each space with no dedicated upstream disconnect, so everything would be a service tap instead of a feeder tap.
I am working on some service load summary calculations for a mixed use building and had a few questions.
I currently have 3-phase 4 wire incoming service that will feeder a 3phase meter bank and single phase downstream residential panels.
Now when sizing a service using the service load calculations are you just sizing the incoming service conductors or do you also size the service tap conductors. Lets say my service calculations for a meter bank and house panel are 260A and the commercial space is 95A. Now I want to remove the house panel from the meter bank and do a direct taps on a wire trough to the service conductors. Is the meter bank tapped at 300A or can I downsize to 250A because I removed the house load and will do a separate service tap. Note I am running the service conductors into a wire trough and service tapping for each space with no dedicated upstream disconnect, so everything would be a service tap instead of a feeder tap.