I got 7-208v 60a ovens and 17-120 12.5 warmers. Need help sizing panel
Yes and I am stuck
I got 7-208v 60a ovens and 17-120 12.5 warmers. Need help sizing panel
If they do draw 60 amps that is correct, if 60 amps just means that size of branch circuit is needed they will be less - but likely not too significantly less. If they just went with next standard size of overcurrent device could be the units draw just over 50 amps, or if they are considered to be continuous load and have an adjusted rating they could even draw down near 40 amps and still call for a 60 amp breaker - that situation can cut your actual current by nearly one third. So you either design your supply for worst case or find out what the actual load is.The current draws I posted are from info giving to me by the company bringing equipment in. I have no eyes on them til they arrive. From plug type listed on specs they are single phase appliances. I did calculations and came up with the kva, then times it by the number of the same unit but it seemed really high. I oven was 12480 kw times 7 unites. Then 87360kw ÷208 =420a. Am I correct?
The current draws I posted are from info giving to me by the company bringing equipment in. I have no eyes on them til they arrive. From plug type listed on specs they are single phase appliances. I did calculations and came up with the kva, then times it by the number of the same unit but it seemed really high. I oven was 12480 kw times 7 unites. Then 87360kw ÷208 =420a. Am I correct?