Load calculations

Status
Not open for further replies.

Elect2011

Member
Location
Reston, VA
I am having a debate in my office and I need your input....I have a multi family building with a garage and some house loads. When I calculate the loads for the house service can I include only the A/C load since it is larger than the Heating load? I know for residential units I can but I don't think I can do that for the house service calculation.


Thanks,
 
I am having a debate in my office and I need your input....I have a multi family building with a garage and some house loads. When I calculate the loads for the house service can I include only the A/C load since it is larger than the Heating load? I know for residential units I can but I don't think I can do that for the house service calculation.


Thanks,

Sure. 220.60 works for all applications.
 