Bill Annett
Senior Member
- Location
- Wheeling, WV
- Occupation
- Retired ( 2020 ) City Electrical inspector
I have a 6 unit apartment building, all units will be the same, each unit has the following.
550 Square feet, 2 small appliance circuits ( 3000VA), one laundry circuit(1500 VA), one dryer (5000VA), Water Heater(4500VA), Range (8000VA) and Heat (6875VA)
I am trying to determine the Service conductor size for this building, The services disconnect will be 6 Breakers ( no main ). I used article 220.84 C and came up with a connected load of 30525 VA for each unit. I then went to table 220.84 and Multiplied 30525 VA by 6 and came up with 183150VA. I then divided it by 240 , I then multiplied that by the demand fact of .44 ( table 220.84 ) which came to 336 Amps.
Am I thinking correctly? It just seems low to me. It has no main , I can picture the tenants getting angry at the owner and turning everything on and we all know what will happen next.
I just want to be sure that my figures are code compliant. Any help will be appreciated.
Thanks, Bill Annett
550 Square feet, 2 small appliance circuits ( 3000VA), one laundry circuit(1500 VA), one dryer (5000VA), Water Heater(4500VA), Range (8000VA) and Heat (6875VA)
I am trying to determine the Service conductor size for this building, The services disconnect will be 6 Breakers ( no main ). I used article 220.84 C and came up with a connected load of 30525 VA for each unit. I then went to table 220.84 and Multiplied 30525 VA by 6 and came up with 183150VA. I then divided it by 240 , I then multiplied that by the demand fact of .44 ( table 220.84 ) which came to 336 Amps.
Am I thinking correctly? It just seems low to me. It has no main , I can picture the tenants getting angry at the owner and turning everything on and we all know what will happen next.
I just want to be sure that my figures are code compliant. Any help will be appreciated.
Thanks, Bill Annett