Just trying to find out the minimum distance an indoor 100a panel can be installed from a deepsink. Working with limited space...may become an issue. Thanks.
No, the working space can be centered to the panel, from left to right, or from right to left, and can even overlap the working space of other electrical equipment. Make sure you can also open the door, if included, to a full 90 degrees.Originally posted by usernotfound:
That 30 inches wide...that's from the edge of of the panel correct? Thanks.