There is a big clash between our US client and me(In India) regarding load calculation .please help me out which is correct.
There is a 120/208V system
8 nos (8x800W)of single phase outgoing feeder.
1 nos of threephase outgoing feeder (4.5kw)
How will you size the incomer here?
a)
A ### B ## C
800 ##800 ##800
800 ##800 ##800
800 ##800 -
1500 #1500 #1500
-----------------------------------
3900 #3900 #3100
-----------------------------------
So the incomer will be based on the total load
3900+3900+3100= 10900 / 1.732*208 = 30.25A
( OR )
b)
A ### B ## C
800 ##800 ##800
800 ##800 ##800
800 ##800 -
4500 #4500 #4500
-----------------------------------
6900 #6900 #6100
-----------------------------------
So the incomer will be based on the maximum load
on the any phase like A (or) B
6900 / 1.732*208 = 19.15 A
Please help me out.
Jeyakumar