Other than the bathroom is their any other room i cant put a load center. single family home ? 2011 nec
 
Closets or Stairways are a no go but other than that as long as you can keep the clearances you are good
Clothes closets. Other closets are permitted and in some cases even preferred. I don't now of an NEC general prohibition of stairwells other than the requirement to guard them and the obvious clear space.
 
Clothes closets. Other closets are permitted and in some cases even preferred. I don't now of an NEC general prohibition of stairwells other than the requirement to guard them and the obvious clear space.
Specifically "stairwells" and "loadcenters" may not be a problem to the letter of the law but generally speaking 240..24..(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway so Dennis' advice will keep him out of trouble.
 
Clothes closets. Other closets are permitted and in some cases even preferred. I don't now of an NEC general prohibition of stairwells other than the requirement to guard them and the obvious clear space.
Of course you are correct. I got slopping and didn't write the word "clothes"


Specifically "stairwells" and "loadcenters" may not be a problem to the letter of the law but generally speaking 240..24..(F) Not Located over Steps. Overcurrent devices shall not be located over steps of a stairway so Dennis' advice will keep him out of trouble.

I never seem to avoid being out of trouble...LOL
 