Load Conduit from top of meter

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is there any CODE restriction to prevent installing a Load side conduit from being installed from the top of a 200 amp meter socket being fed from an underground lateral..
It appears there would not be a problem based on 312.6(B)(2) exceptions.
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
Is there any CODE restriction to prevent installing a Load side conduit from being installed from the top of a 200 amp meter socket being fed from an underground lateral..
It appears there would not be a problem based on 312.6(B)(2) exceptions.
No sir! No code restrictions.

Ron
 