G gbarone Member Location Southampton, PA Dec 8, 2012 #1 I have a generator transfer switch with a load control module. Need to know where to connect the wires on the air handler terminal block. Appreciate any help, thanks.
I have a generator transfer switch with a load control module. Need to know where to connect the wires on the air handler terminal block. Appreciate any help, thanks.
JoeStillman Senior Member Location West Chester, PA Dec 11, 2012 #2 The Air Handler most likely doesn't have terminals dedicated to that function. Look for a place where you can interrupt control power, like maybe downstream of the CPT fuse.
The Air Handler most likely doesn't have terminals dedicated to that function. Look for a place where you can interrupt control power, like maybe downstream of the CPT fuse.
J Joe Villani Senior Member Location Westchester County NY Dec 11, 2012 #3 Load Control Module Load Control Module JoeStillman said: The Air Handler most likely doesn't have terminals dedicated to that function. Look for a place where you can interrupt control power, like maybe downstream of the CPT fuse. Click to expand... If this is a hydro air system you will lose heat. I would just break the "Y" terminal/wire going to the condensing unit.
Load Control Module Load Control Module JoeStillman said: The Air Handler most likely doesn't have terminals dedicated to that function. Look for a place where you can interrupt control power, like maybe downstream of the CPT fuse. Click to expand... If this is a hydro air system you will lose heat. I would just break the "Y" terminal/wire going to the condensing unit.