Suppose I've been asked to approve a drawing showing a feeder (3-ph, 480 V) fed from a given panel's spare 50 A breaker. There are no details yet on what the load will be; that will come at a later point, and be subsequently approved. I only know that it will further feed a sub-panel that has yet to have been finalized. Suppose I determine the ampacity of this feeder (taking the lower of the calculated ampacity at the middle of the wire and at the terminations)(considering appropriate ambient temperature derating, etc.) to be 44 A. I therefore approve connection to / use of the proposed 50 A breaker, as allowed per 240.4(B).
I now have a situation where someone in the future can specify that downstream load (sub-panel), say with a 50 A main breaker, and there is a chance that load on that sub-panel may creep up over time to 49 A. I've now exceeded the ampacity of the upstream feeder, and I would expect unacceptable temperature rise (somewhere on that conductor).
Is it right to expect and count on future engineers to determine and check upstream feeder ampacities to see if they are impinging on this "upsize wiggle room"? Do you as an engineer do it? I believe people are often only focused on what they are immediately connecting to and what they are installing. Perhaps this is reason to challenge that approach.
Even if some load information is known, there is always the chance that small incremental load can impinge on this "upsize wiggle room".
Perhaps there are enough layers of conservatism built into the NEC requirements below 800 A that this is a non-issue.
I now have a situation where someone in the future can specify that downstream load (sub-panel), say with a 50 A main breaker, and there is a chance that load on that sub-panel may creep up over time to 49 A. I've now exceeded the ampacity of the upstream feeder, and I would expect unacceptable temperature rise (somewhere on that conductor).
Is it right to expect and count on future engineers to determine and check upstream feeder ampacities to see if they are impinging on this "upsize wiggle room"? Do you as an engineer do it? I believe people are often only focused on what they are immediately connecting to and what they are installing. Perhaps this is reason to challenge that approach.
Even if some load information is known, there is always the chance that small incremental load can impinge on this "upsize wiggle room".
Perhaps there are enough layers of conservatism built into the NEC requirements below 800 A that this is a non-issue.