In my last test in Oregon there was a 10 units 1000 SQFT dwelling calculation. Each with 10KW range and 10KW heater. I came up with 169KW demand for this building using optional. There will be 480/208 3 phase transformer. now
1. Is optional method ok if didn't tell me which one to use?
2. I need only 169KW and next standard 3 phase is 225KVA, and is that the right choice?
3. So if I go with 225KVA then that is 625A and do I size OC at 125%? I heard I can size the secondary OC at lower size.
What size OC disconnect? (A)600A, (B)700A, (C)800A, (D)1000A.
If I size the OC at 125% it will be 800A but even 500A is enough for this building.
1. Is optional method ok if didn't tell me which one to use?
2. I need only 169KW and next standard 3 phase is 225KVA, and is that the right choice?
3. So if I go with 225KVA then that is 625A and do I size OC at 125%? I heard I can size the secondary OC at lower size.
What size OC disconnect? (A)600A, (B)700A, (C)800A, (D)1000A.
If I size the OC at 125% it will be 800A but even 500A is enough for this building.