- Lockport, IL
- Semi-Retired Electrical Engineer
Proposal:
Add a definition under Article 100 for ?Load Diversity.? As an alternative, replace the phrase ?load diversity? in the five locations at which it presently appears in the NEC, by substituting a phrase that more accurately and clearly conveys the intended meaning.
Substantiation:
The phrase "load diversity" appears in five locations, and the word "diversity" appears nowhere else. Two of the locations are within Table B310.11. Two of the locations are in Fine Print Notes ? associated with 310.15(B)(2)(a) and 400.5 ? that refer the reader to Table B310.11. The fifth location is in Table 520.44. In all five locations, the reader is led to believe that a higher value of ampacity can be justified if the ?load diversity? is 50% or lower.
The NEC does not define ?load diversity.? It is understood that if a term or phrase is not explicitly defined in the NEC, then the reader is to interpret that term or phrase in accordance with common industry usage. However, the phrase ?load diversity? does not possess a common industry usage for which a calculated result could be expressed as a fraction less than one.
There are two commonly used definitions of ?diversity,? as applied in connection with electrical load.
There are two problems with leaving this term in the NEC without a useful definition: First, we have what appears to be an available alternative for calculating ampacity, but the alternative is useless and meaningless. This leads to the second problem: that someone might try to take advantage of this alternative, but do it incorrectly, and thereby install a system that is undersized for its intended loading conditions.
I can present no evidence that an incorrect application of the allowance for ?load diversity? has ever led to the installation of an unsafe system. But it is clear that present wording, and the present lack of a clear definition, (1) cannot lead a person to do it right, and (2) can lead a person to do it wrong.
Substantiation:
?Load Diversity? is defined as, ?The difference between the sum of the maximum of two or more individual loads and the coincident or combined maximum load, usually measured in kilowatts.?
The first of these terms cannot be expressed as a dimensionless ratio. It is measured in units of power. The second of these terms is a ratio that must necessarily be greater than or equal to 1.0. Therefore, the concept of ?a load factor of 50%? is meaningless.?Diversity Factor? is defined as, ?The ratio of the sum of the individual maximum demands of the various subdivisions of a system to the maximum demand of the whole system.?