I'm trying to figure out the service requirements for 200 stoves at 8320w service is 120/208 3 phase
Engineer is coming up with 800 amps and I want to double check
I'm having a bit of a hard time looking through example D5(a) and not sure howntheytare coming up with "maximum number between two phase legs" can some one explain
And I do think that a demand factor of 26% is required According to 220.55
Sent from my SM-G965U using Tapatalk