I have load of 120V which is being fed from 2P 20A breaker 2 ph conductors, 1 neutral and one ground. In between I have 240V fused disconnect with 2 fuses.

One of the fuses and one of the breakers would not have any load.
I am wondering is their anything in NEC that requires this install to have 1 ph conductor 1 neutral and 1 ground?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So you have a single phase 240 volt circuit with a neutral feeding a disconnect switch and there is only a 120 volt load connected?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I am wondering is their anything in NEC that requires this install to have 1 ph conductor 1 neutral and 1 ground?
No. I'm curious as to why would you think that? The unused conductor in the disconnect is just a spare.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
No. I'm curious as to why would you think that? The unused conductor in the disconnect is just a spare.

Shheesh now electrical designer says disconnect serves auxiliary load and the chair lift both. Didnt even provide what type of auxiliary load phase voltage nothing. Is this strange auxiliary loads for chair lift?
 