http://static.schneider-electric.us...nsulated Case Circuit Breakers/0600DB0101.pdf
Considering the White Paper above, We have a distribution panel with 100% breakers that will be serving continuous loads.
One of the 100% rated breakers (400A) in the DP panel will feed a 400A MLO panelboard. Although the 100% rated breaker is listed / tested in the DP panel, the downstream MLO panel doesn't have any special testing and will draw up to 400A of continuous load.
Do you see an issue? Is a regular MLO panel capable of 100% loading? I don't know of any such 100% rating for a MLO panelboard on its own.
Considering the White Paper above, We have a distribution panel with 100% breakers that will be serving continuous loads.
One of the 100% rated breakers (400A) in the DP panel will feed a 400A MLO panelboard. Although the 100% rated breaker is listed / tested in the DP panel, the downstream MLO panel doesn't have any special testing and will draw up to 400A of continuous load.
Do you see an issue? Is a regular MLO panel capable of 100% loading? I don't know of any such 100% rating for a MLO panelboard on its own.