I have two parallel 4/500 with 2 1/0 grd cables each feeding a 120/208 3 phase feeding an 800 AMP MDP.
During maintenance check found 26 amps on grounding condutors going back to the Generator. The main bonding jumper is a 4/0 from ground bar to neutral bar in MDP with 4/0 grd loop with five grd rods.
Question why would I have a load of 26 amps on ground and only 10 amps on the 500 mcm neutral.
Lost in Afghansitan.
During maintenance check found 26 amps on grounding condutors going back to the Generator. The main bonding jumper is a 4/0 from ground bar to neutral bar in MDP with 4/0 grd loop with five grd rods.
Question why would I have a load of 26 amps on ground and only 10 amps on the 500 mcm neutral.
Lost in Afghansitan.