Load Shedding Breakers without Generator

Status
Not open for further replies.

anachnujr

Member
Location
SF, CA, USA
Hi all-

Does anyone know of a residential Load Shedding system that will shut off non-priority loads? The idea here is to install a high current EV Charger (non-priority load) without upgrading the electrical service.

I've seen a few products made by Kohler, but I think they all need to be installed alongside an ATS.

Thanks.
 
Hi all-

Does anyone know of a residential Load Shedding system that will shut off non-priority loads? The idea here is to install a high current EV Charger (non-priority load) without upgrading the electrical service.

I've seen a few products made by Kohler, but I think they all need to be installed alongside an ATS.

Thanks.

I think you got it right with the ATS. Or you could manually turn off breakers, but that is damn inconvenient. Hopefully others will chime In.
 
If main breaker is overloaded enough it trips, that will result in total load shedding:D

I suppose you could use a current sensing relay and set it to operate a contactor to shed load when a certain level is reached- but to work best you need it to not monitor the load being shed or as soon as you cut off that load - you may drop enough current that it is then able to come back on which will result in rapid cycling - not going to work out so well there. So this is likely going to involve monitoring one service or feeder conductors that supply the main premises loads and having a second service or feeder conductors not being monitored that supplies the load(s) to be shed.

ETA: of course you were trying to avoid upgrading service so that suggestion is not going to be all that acceptable, and may cost more then a simpler service upgrade anyway. Other alternative may not be so cost effective either - is to have more logic processing available in whatever you come up with to control things - I'm sure something can be done for a price - but is still likely higher then a simpler service upgrade.

Maybe you can leave existing equipment as is and properly add a second through sixth service disconnecting means and supply these loads from that?
 