I have a site with 200A service into a Milbank 200A meter/main combo, with conductors from meter entering 200A main breaker at top of 200A busbar, lugs at the bottom of the busbar feeding a 200A house panel with 200A main breaker in it. Also on the meter main bus is a 100A breaker feeding an outbuilding, installed near top right of meter main. There are two open positions for a 240V backfed breaker for solar.
So considering the meter main:
200A can come down into bus from utility, limited by the main breaker
200A can exit the bus through the bottom lugs, limited by the house panel main breaker
100A can exit the bus to feed the outbuilding, limited by the breaker near top right of bus
48A x 1.25 = 60A can enter the bus, if I installed a 60A breaker at lower left position for the solar
No where on this bus is it possible to see more than 200A. Do you agree?
I believe, and ask for confirmation from you all, that 705.12(B)(2)(3)(c) of 2017NEC permits the above. The sum of the load and source breakers on the bus, 100A + 60A, excluding the 200A main that protects the bus is 160A which does not exceed the 200A busbar rating.
I also considered the following options:
A. Supply-side connection using Ilsco taps on the conductors between meter and main, but this would violate UL and not much room to do it.
B. Downsize main breaker from 200A to 175A with backfed breaker to keep within the 120% rule of 705.12(B)(2)(3)(b) of 2017 NEC. But this breaker cannot be found.
C. Load side connection by tapping the feeder to the house within the meter main enclosure.
I want to be prepared when I submit the permit and grid connection applications in case I get pushback so any advice would be appreciated.
So considering the meter main:
200A can come down into bus from utility, limited by the main breaker
200A can exit the bus through the bottom lugs, limited by the house panel main breaker
100A can exit the bus to feed the outbuilding, limited by the breaker near top right of bus
48A x 1.25 = 60A can enter the bus, if I installed a 60A breaker at lower left position for the solar
No where on this bus is it possible to see more than 200A. Do you agree?
I believe, and ask for confirmation from you all, that 705.12(B)(2)(3)(c) of 2017NEC permits the above. The sum of the load and source breakers on the bus, 100A + 60A, excluding the 200A main that protects the bus is 160A which does not exceed the 200A busbar rating.
I also considered the following options:
A. Supply-side connection using Ilsco taps on the conductors between meter and main, but this would violate UL and not much room to do it.
B. Downsize main breaker from 200A to 175A with backfed breaker to keep within the 120% rule of 705.12(B)(2)(3)(b) of 2017 NEC. But this breaker cannot be found.
C. Load side connection by tapping the feeder to the house within the meter main enclosure.
I want to be prepared when I submit the permit and grid connection applications in case I get pushback so any advice would be appreciated.