I have a question regarding a Load Side PV feeder Tap. Not a Line Side tap to be clear. And this is not a breaker connection.
Situation is a customer has a meter/main combo and there isn’t space to tap what would be considered the line side(ahead of the main breaker) before the 200A main breaker. From that main breaker the feeders run into a 225A main lug load center inside the house not really accessible and no room for backfed breaker.
Installing 31 enphase IQ7PLUS micro inverters. Which comes out to roughly 47A with the safety adder. (1.5a x 31 micros )
Is it ok to tap the load side of the feeders( after the 200A main) ? What needs to be taken into consideration? There’s just not much I could find online regarding this situation and I do understand speaking with the local AHJ is best course. But he’s a hard man to pin down and I’m curious what the general consensus is.
Situation is a customer has a meter/main combo and there isn’t space to tap what would be considered the line side(ahead of the main breaker) before the 200A main breaker. From that main breaker the feeders run into a 225A main lug load center inside the house not really accessible and no room for backfed breaker.
Installing 31 enphase IQ7PLUS micro inverters. Which comes out to roughly 47A with the safety adder. (1.5a x 31 micros )
Is it ok to tap the load side of the feeders( after the 200A main) ? What needs to be taken into consideration? There’s just not much I could find online regarding this situation and I do understand speaking with the local AHJ is best course. But he’s a hard man to pin down and I’m curious what the general consensus is.